    I have a 220v line running to a disconnect box to the back of my house that was formally for a hot tub. I want to move the line and disconnect inside my garage and run some 220v outlets to run some 220v tools. Can I run more than 1 220 v outlet off of that breaker? It is a 50a breaker, so it should be able to handle a pretty big load, but I want to stay safe. There is a very good chance that more than one tool would be on at once, but adding the total watts together at max draw wouldn't begin to approach 75% of the 50a rating.

    Thanks
     

    kcinnick

    Training Ferrous Metal
    Rating - 100%
    28   0   0
    Dec 24, 2008
    4,723
    38
    Baton Rouge
    Nope, no welding in my near future. I am thinking the 50A is way overrated for what I need, but it is already there, and I even have the disconnect box. I figure I can move the disconnect box to the garage and run 4 outlets so I don't have to plug stuff in and out all the time, it is a small move and I don't have to do much wiring work to get 220 to my garage and shop.

    Even if I did get a welder, would I be OK if that was the only tool running? I have no plans of getting one.
     

    edman87k5

    Well-Known Member
    Rating - 100%
    35   0   0
    Oct 22, 2007
    2,625
    38
    Ventress, LA
    Depends on the welder. I would use a drop box with separate breakers for each piece of equipment myself.
    Much safer and only a few extra bucks to do.
     

    dhfischerjr

    Well-Known Member
    Rating - 100%
    1   0   0
    Apr 8, 2012
    46
    6
    Pearl River
    Most welders require a 60Amp line. All of the welding outlets in my shop have dedicated breakers.
     

    Yrdawg

    *Banned*
    Rating - 0%
    0   0   0
    Sep 24, 2006
    8,386
    36
    Big Woods
    Make sure the wire from your source is rated for 50A . Wire size and breaker size for each outlet need to be same rating. You can run a circuit with several outlets on one breaker as long as the wire size is correct. Also you probably don't have a neutral and ground in the configuration so don't look to add any 115v loads in this. If you ever expect to sell you might want to make sure whatever you do is up to code for future inspections.

    You might be happier in the long run coming from home panel with 4 wire 60 a ckt to a new sub panel in your shop.
     

    jmaroon

    Member
    Rating - 0%
    0   0   0
    Apr 18, 2012
    16
    1
    breakers are cheap and easy to change.. if you don't need 50 amps, go to home depot and get another 220 breaker rated more for what your going to use.. it'll be cheaper than running #6 wire to an air compressor when all you need is 8g (30 amps)or 10g.. (20 amps).. or like one poster said.. run a sub panel off of the 50a 220..
     

    kcinnick

    Training Ferrous Metal
    Rating - 100%
    28   0   0
    Dec 24, 2008
    4,723
    38
    Baton Rouge
    Make sure the wire from your source is rated for 50A . Wire size and breaker size for each outlet need to be same rating. You can run a circuit with several outlets on one breaker as long as the wire size is correct. Also you probably don't have a neutral and ground in the configuration so don't look to add any 115v loads in this. If you ever expect to sell you might want to make sure whatever you do is up to code for future inspections.

    You might be happier in the long run coming from home panel with 4 wire 60 a ckt to a new sub panel in your shop.

    breakers are cheap and easy to change.. if you don't need 50 amps, go to home depot and get another 220 breaker rated more for what your going to use.. it'll be cheaper than running #6 wire to an air compressor when all you need is 8g (30 amps)or 10g.. (20 amps).. or like one poster said.. run a sub panel off of the 50a 220..

    I will probably get a new panel in the next couple of years when I get some other upgrades done, I just figured this was a cheap and easy way to get a few 220 outlets for now.

    The wire is pretty thick, I haven't checked the gauge of the wire, but it was running a pretty large hot tub I had removed when I bought the house.
     

    cajun 22

    Shooter
    Rating - 100%
    40   0   0
    May 22, 2008
    1,497
    48
    Houma, LA
    More than likely the wire is a 6/3 with ground for a hot tub. Turn the breaker off, open the disc., check to see if there is a black/red/white/bare ground in the box. If so you can relocate this wire to the garage and install a small panel. Then you can run the proper size line to each device you wish to run and install the proper size breaker also. Just remember to get a panel with two ground bars and bond one to the panel for the ground. The other will not be bonded to the panel and all of the neutral/white wires will go here if you need a 110v line.
     

    kcinnick

    Training Ferrous Metal
    Rating - 100%
    28   0   0
    Dec 24, 2008
    4,723
    38
    Baton Rouge
    More than likely the wire is a 6/3 with ground for a hot tub. Turn the breaker off, open the disc., check to see if there is a black/red/white/bare ground in the box. If so you can relocate this wire to the garage and install a small panel. Then you can run the proper size line to each device you wish to run and install the proper size breaker also. Just remember to get a panel with two ground bars and bond one to the panel for the ground. The other will not be bonded to the panel and all of the neutral/white wires will go here if you need a 110v line.

    That is the type of line it has. It had a wire going to a grounding rod when I removed the wiring coming from the disconnect to where the hot tub was located. I just left the rest of the wiring in place.

    So I can wire this hotub wire to my garage (well car port, with shop on the side, looking at enclosing options now, some type of door or wall), instead of putting it to a disconnect and running one circuit I can put in a panel with 4 breakers as long as the total doesn't exceed 50a? The slot says 70a max, but has a 50a GFIC breaker, if I were to go with 4 15a breakers would it be as easy as just switching the breaker to 60a? the run is going to be about 50% or more shorter than the current run, so I should have plenty of wire left over to work with, and I still have the wires that ran from the house to the hot tub.
     

    mpl006

    Well-Known Member
    Rating - 100%
    1   0   0
    Nov 4, 2011
    386
    16
    Ruston
    You could put in 4 15 amp breakers in the new panel while leaving the main breaker at 50 A. The total amount of the breakers in the panel does not have to be less than the breaker feeding the panel, you just would not be able to run all circuits to full rating if the total branch circuits does exceed the main. If you raise the 50 A to 60 you would possibly have to upgrade the wire size.


    Sent from my iPhone using Tapatalk
     

    cajun 22

    Shooter
    Rating - 100%
    40   0   0
    May 22, 2008
    1,497
    48
    Houma, LA
    Just count the number of circuits that you want to run. If you need three 220v lines you would need at least 6 circuits. You can get a 12 circuit main lug panel and run the lines you need. It will be derated to the amperage of the breaker, in your main panel, feeding the hot tub line. You won't need a main if it is 6 or less movements of the hand (breakers). You won't need GFCI breakers if the plugs are for dedicated service i.e., table saw, planer, air.comp., and such. You only need GFCI for general use 110v recepticals, if it is in a garage or open to the outside. 50amps per leg is a lot of juice to pull. It could happen but how many tools can you operate at once?
     
    Last edited:

    kcinnick

    Training Ferrous Metal
    Rating - 100%
    28   0   0
    Dec 24, 2008
    4,723
    38
    Baton Rouge
    You could put in 4 15 amp breakers in the new panel while leaving the main breaker at 50 A. The total amount of the breakers in the panel does not have to be less than the breaker feeding the panel, you just would not be able to run all circuits to full rating if the total branch circuits does exceed the main. If you raise the 50 A to 60 you would possibly have to upgrade the wire size.


    Sent from my iPhone using Tapatalk

    Just count the number of circuits that you want to run. If you need three 220v lines you would need at least 6 circuits. You can get a 12 circuit main lug panel and run the lines you need. It will be derated to the amperage of the breaker, in your main panel, feeding the hot tub line. You won't need a main if it is 6 or less movements of the hand (breakers). You won't need GFCI breakers if the plugs are for dedicated service i.e., table saw, planer, air.comp., and such. You only need GFCI for general use 110v recepticals, if it is in a garage or open to the outside. 50amps per leg is a lot of juice to pull. It could happen but how many tools can you operate at once?

    Awesome.

    I only needed 1 220v outlet, but then it was suggested that I could run more than one from that line, and I just wanted to confirm. Two will be much more convenient, but if I am going to put two, I might as well go with as many as I can get so I have options in the future. All the 220v lines will be in the shop portion, the carport is not enclosed to a garage yet, but will be in the future. 4 15's should be plenty since the shop space is only 6'X20'. Why oh why did they not make it at least 8' wide I will never understand.

    I am not using your typical shop tools, as my hobbies don't use typical shop tools, but a 220 Air Compressor is on the list along with a 220 Convection oven.
     

    kcinnick

    Training Ferrous Metal
    Rating - 100%
    28   0   0
    Dec 24, 2008
    4,723
    38
    Baton Rouge
    I have 6 AWG cable coming in. Can I replace the 50a breaker with a 60a breaker? I would also like to have 6 outlets, would it be best to put each one on its own breaker in a breaker box, some will need 30a, some only need 15a. I will never use everything at once, I just want the flexibility to have the outlets where I need them without having move things around or plug and unplug different outlets.

    Thanks
     

    VeedUp

    Well-Known Member
    Gold Member
    Rating - 100%
    54   0   0
    Oct 15, 2007
    3,329
    38
    Destrehan, La.
    i have 6 awg cable coming in. Can i replace the 50a breaker with a 60a breaker? i would also like to have 6 outlets, would it be best to put each one on its own breaker in a breaker box, some will need 30a, some only need 15a. I will never use everything at once, i just want the flexibility to have the outlets where i need them without having move things around or plug and unplug different outlets.

    Thanks

    yes you can, you need to run a sub panel as suggested above earlier so you can run your 120 outlets off of the service you have.
     

    kcinnick

    Training Ferrous Metal
    Rating - 100%
    28   0   0
    Dec 24, 2008
    4,723
    38
    Baton Rouge
    yes you can, you need to run a sub panel as suggested above earlier so you can run your 120 outlets off of the service you have.

    Everything new will be 220. I already have 110 ran. What do I do with the extra ground wire? it was there to go to a grounding rod, do I need to to something with it or can I leave it alone?
     

    Hitman

    ® ™
    Rating - 100%
    13   0   0
    Sep 4, 2008
    16,034
    36
    Lake Charles
    I just figured this was a cheap and easy way to get a few 220 outlets for now.
    .

    Awesome.
    I only needed 1 220v outlet, but then it was suggested that I could run more than one from that line,

    I'm pretty sure you are getting some bad information here.

    I say this b/c I moved my Laundry Room into a portable shed outside the home. Had to run a 220 for the Dryer.
    Then we wanted to put a 220 A/C w Heater so the shed is temp controlled.

    I was told by an electrician, and my father-n-law who also runs wire, that I should NOT just tap into the 220 outlet and make another outlet for the A/C to plug into. I was told I would have ot run a completely new 220 line.

    The reason;
    1- Say it's a 50 Amp breaker and the dryer is taking up half that are more already, when the A/C kicks on *boom* Breaker Trips. Tripping breakers is a safety of course but not something you want to make a habit of and you better hope it does trip b/c if it doesn't you'll have a serious problem on your hands and you might find out once your box explodes and the house is on fire. Not being scary, I work with some electricians and they tell REAL stories all the time.
    2- Now it is possible to have two 220 outlets off one line "IF" you have the proper size wire that will then allow you to put a 100 Amp breaker for that circuit.

    What you need to do is simple. Call a local electrician, tell him what you want to do and see what he says or if he'll drop by and take a look.

    *NOTE* I just hung the phone up with the head A/C Tech & Electrician for Fort Polk. He reassured me of all what I just posted.

    Your case could be different, he's a nice fellow if you want his number PM me and you can call him yourself. ;)

    ...and to be honest the LAST place I would look to for advice on Electricity is the INTERWEBZ
    oups-pardon-9877.gif
     
    Last edited:

    VeedUp

    Well-Known Member
    Gold Member
    Rating - 100%
    54   0   0
    Oct 15, 2007
    3,329
    38
    Destrehan, La.
    I don't think anyone told him to run the 220 outlets in series with one another, he can definitely run a 60amp breaker on the #6 and put a small sub panel in and run a compressor and something else off of it, but without really looking at it and seeing his panel and all its hard to really give good advice, but hot tubs and anything that uses a heating element draws a lot of amps. so it would need a large breaker for an oven(60 or 50 amp) or something like a heater, unless its something small like a water heater which most can run on a 30amp breaker. I was just answering the one question about the #6 handling a 60 amp breaker, but he should definitely consult with a professional before trying to tackle it himself.
     