    My current generator is a 5600 watt continous output. On the tag it says 23 AMP output at 240 volts. I use the 30 AMP / 240v twist lock plug into my 30 AMP breaker. So my question is that if I am only running items that use 120 volts, I should be able to pull a total of 46 AMPs at 120 volts? Is that correct?
     

    kibb

    Well-Known Member
    Rating - 100%
    1   0   0
    Jul 19, 2010
    184
    18
    Lafayette, La
    Sounds right. Be careful when pulling heavy loads and running compressors/motors. Try to keep it at 60 hz.
     
    Last edited:

    themcfarland

    tactical hangover
    Rating - 100%
    58   0   0
    Dec 6, 2008
    4,665
    63
    Destrehan
    are you trying to run both 30 amp cord and your 15 amp 110 v plugs at same time?

    if you use the 30 amp plug, the hots from the 110v go to make up the legs for 240
     

    toddrod

    Well-Known Member
    Rating - 100%
    9   0   0
    Feb 14, 2007
    1,754
    36
    Vacherie, LA
    I think he asking about 46 off the house breaker after he feeds it from the 240 off the genny.

    This is correct. I am going to be getting a bigger genset and I am trying to figure out if I want to go 8KW or 10 KW continous output. I will not be runninig my central A/C off of this.
     

    BillnLA

    Well-Known Member
    Rating - 100%
    10   0   0
    Jun 24, 2009
    113
    18
    Albany
    My current generator is a 5600 watt continous output. On the tag it says 23 AMP output at 240 volts. I use the 30 AMP / 240v twist lock plug into my 30 AMP breaker. So my question is that if I am only running items that use 120 volts, I should be able to pull a total of 46 AMPs at 120 volts? Is that correct?

    Someone can correct me if I state something wrong. I believe this to be correct based upon my electrical knowledge but am not an electrician.

    Yes but not quite. Your generator's windings have two 120 volt "sides" or feeds, just as your incoming power does. What it will supply to each 120 volt "side" is half of its total output or 2800 watts. So you can't pull the total 5600 watts from one winding. Your electrical load will need to be somewhat divided between the two sides or it can overload one winding on the generator. Every other circuit breaker on one side of the electrical panel is connected to one "side". The others on the same side are connected to the other 120v side. So, on the left side of your panel will be breakers " 1,3,5 etc. Every other slot, 1,5,9,etc. will be on the same load "side". On the right side will be the even numbered breakers, but the same applies.
     

    kibb

    Well-Known Member
    Rating - 100%
    1   0   0
    Jul 19, 2010
    184
    18
    Lafayette, La
    The 240 is drawing from both 120s to add up to 240. He can pull it all from the 240 as long as the 120 is left alone. This is correct isn't it?
     
    Last edited:

    kibb

    Well-Known Member
    Rating - 100%
    1   0   0
    Jul 19, 2010
    184
    18
    Lafayette, La
    The wires are connected to common bars in the box. It shouldn't make a difference where the live breakers are located in the panel.
     

    drumz2129

    Well-Known Member
    Rating - 100%
    2   0   0
    Jul 29, 2009
    886
    16
    Sulphur, La.
    What bill is saying is correct. Let me try to explain this clearly. Let's ignore voltage drop from wire length and connections.

    Feeding you house from the electric company is a 220v - 200A (usually) service. This is made up of two 'legs' of 120volt power with respect to neutral with a 180deg phase difference. This means there is 120V running down each buss in the breaker box, L1 and L2. To achieve 220V. a double pole breaker is tied to both the L1 and the L2 buss and since each 120V bus is 180deg out of phase with each other it gives a voltage potential of 240V.

    When you remove the electric company service and replace it with your generator, you will have a 240V - 23A service. You will have 23A capacity on each bus in the breaker box. If only running 120v items, you will have the capacity of 46A @ 120V, but it has to be evenly distributed between the two busses to evenly load each leg of the generator. This can be tricky if you do not know the power draw of each item you are using, along with knowing which buss each circuit in your house is tied to to make sure you have an balanced load on the generator.
     

    charliepapa

    Clandestine Sciuridae
    Rating - 100%
    130   0   0
    Jul 12, 2009
    6,155
    38
    Prairieville
    The wires are connected to common bars in the box. It shouldn't make a difference where the live breakers are located in the panel.

    I don't think so. the "bars" in the box come up and are connected to every other spot in the box. the single breakers that feed 120V requirements only connect to one spot or one of the bars. the 240V requirements use double breakers that connect to two spots, one side on each of the two bars.

    breaker-panel.gif
    IMG00102-1024x768.jpg
     
    Last edited:

    drumz2129

    Well-Known Member
    Rating - 100%
    2   0   0
    Jul 29, 2009
    886
    16
    Sulphur, La.
    I don't think so. the "bars" in the box come up and are connected to every other spot in the box. the single breakers that feed 120V requirements only connect to one spot or one of the bars. the 240V requirements use double breakers that connect to two spots, one side on each of the two bars.

    breaker-panel.gif
    IMG00102-1024x768.jpg

    :hi5: good illustration.
     

    cajun_64

    Well-Known Member
    Rating - 100%
    19   0   0
    Mar 22, 2012
    655
    18
    Abbeville
    The drawing is incorrect.
    If you look inside the panel, at the upper most spots(breakers 1 and 2) both breakers are attached to the same buss. As an example phase A
    Breakers 3 & 4 will be attached to phase B
    breakers 5 & 6 will be attached to phase A
    etc. etc.

    Odd numbers are on the left, even are on the right
    This should be consistant unless you install the piggy back/slim line breakers.
     
    Last edited:

    flamatrix99

    Well-Known Member
    Rating - 100%
    62   0   0
    Oct 7, 2008
    5,282
    48
    Zachary, La
    if you use the 30 amp plug, the hots from the 110v go to make up the legs for 240

    from your 240v genney you have 120v 23amp on each bus in your breaker panel.

    A single pole breaker only comes off of one bus. Say for a bedroom circuit. Two pole breakers say for your A/C come off of both buses to give you 240v.

    dantheman would be the one to ask though.
     
    Last edited:

    kibb

    Well-Known Member
    Rating - 100%
    1   0   0
    Jul 19, 2010
    184
    18
    Lafayette, La
    ^This. I had a brain fart earlier. The genny feeds both bars therefore, they aren't common. The load has to pull from two different 120 sources to get 240 meaning 2 different buses.
     

    bayoupirate

    God of Thunder
    Rating - 100%
    8   0   0
    Jul 9, 2009
    1,230
    36
    Raceland, Louisiana
    What are you planning on running?
    Fridge, freezer, lights, tv, computer and a couple of window units?
    Figure out your watt/amp load. Whatever the a/c unit(s) are rated for, double that for amps needed to start-up.
    Be sure that the new gen can make that rating continou.
    You want that extra for start-up. If you get a
    g


    enerator with just enough capacity, you'll be running it hard always. Thats not good on any of the components.
    Running at about 50 to 70%. is most efficient.
     